Lets talk a moment on this... National Electric Codes say not to use more than 80% of the capacity of the breaker/outlet. So this will limit you a little. Actual line voltage varries from 115 to 120 volts... Garas is right... P(watt) = I (amps) x V (volts)
15 amp outlet requires at least a #14 wire, 80% of apx 1800 W = 1400 watts max
20 Amp, requires #12 wire; 80% of apx 2400W = 1920W Max
Most household outlets are 15 amps. However, my house is wired with 15 amp outlets, on a 20 amp breaker. This would allow me to a change the outlet to a 20 amp if I wanted to or would give me the ability to have a total load under the 1920 max. However since the outlets are 15 amp I have to respect the load limits of 1400 watt max.
So you need to start with the breaker and see what it says. Then look at the outlet. If the outlet if a 15 A and the breaker is a 20A (the wire should be a #12 if attached to a 20 A breaker) You can upgrade to a 20A outlet. I would double check the wire size before doing this.
As also stated, most surge protectores are 15 amps. Make sure you do not over load them. It is possible to pull more than the posted load through a breaker which can cause excessive heat and can be dangerous.
HTH