Reef Sanctuary
Become a Sponsor   Our Sponsors  

Welcome to the Reef Sanctuary forums.

We're a beginner-friendly Reef Aquarium community featuring saltwater fish tank discussion, reef aquarium supply reviews, free photo gallery and more!

You are currently viewing our boards as a guest which gives you limited access to many of our features. Registration is fast, simple and absolutely free so please, join our community today! Want to check the place out first? Take a look at our Beginner's Guide for a quick tour of all the features we have to offer the marine aquarium hobbyist. If you have any problems with the registration process or your account login, please contact contact support.

Go Back   Reef Sanctuary > Main Forums > Equipment
User Name
Password
Home Forums Photo Gallery Chat Product Reviews Live Coral Frags Register Search Today's Posts Mark Forums Read

Equipment Discuss reef aquarium equipment including filtration, lighting, pumps, etc.

Reply
 
LinkBack Thread Tools
Old 02-08-2007, 10:36 PM   #16 (permalink)
sebastian
Sea Pen
 
sebastian's Avatar
 
Join Date: Feb 2007
Location: lake zurich, il
Posts: 341
Re: electrical

as a painter point of view.... always tape outlets
__________________
Sebastian
member of CMAS

125G AGA + 30G sump (home made)
500W MH + 260W PC light
Wave 2K (4,000 g/h), mag-drive 12 (1,000 g/h)
Euro reef skimmer
Hammer corals, zoo's, green star polyps, neon green button polyps, blue acro, green staghorn, frogspan, leathers, xenias, 100's mashrooms, ricordias, fungias, green oxypora, neon green hydropora, snake polyps, brown Caribbean zoanthid (palythoa carribaeorum)

regal tang, yellow tang, six line wrasse, cleaner wrasse, (2) lyretail anthias, eibli angel, ocellaris clown
sebastian is offline   Reply With Quote
ReefSanctuary Sponsor
Old 02-08-2007, 11:08 PM   #17 (permalink)
emo_1992
Bryozoan
 
emo_1992's Avatar
 
Join Date: Jan 2007
Location: Idaho Falls, ID
Posts: 47
Re: electrical

That is one of my biggest pet peeves painted outlets and light switches. I have replaced so many when we have moved into new places. Always tape them befor painting. The good news is you know the gfi works.
emo_1992 is offline   Reply With Quote
Old 02-09-2007, 03:12 AM   #18 (permalink)
deaclauderdale
Posting & Toasting!
 
deaclauderdale's Avatar
 
Join Date: Jun 2006
Location: Lancaster,California
Posts: 2,049

My ReefSpace
Add yours!
Re: electrical

Quote:
Originally Posted by billyr98 View Post
Ok well you want to run a couple circuits at least on a bigger system.. 200g +
But you need to give me some info on your equipment... Lighting and such...

I ran one 20amp circuit for lighting.. 1 20amp circuit for Powerheads and Misc stuff under the tank..

And one more 20amp circuit for my main pump, skimmer and such stuff...

If you have 15amp breakers already, run 14/2 wire and if not run 12/2 and use 20 amp breakers.. any questions ask away, I do it for a living...

Billy do you have any pics of your electrical setup?
__________________
100 Gal w/ 55 Gal Sump, (2) 250 watt MH's, 220 watts VHO,

Fish: Lawnmower Blenny, Pair Ocellaris Clowns, Royal Gramma, Yellow Watchman Goby, Rainsford Goby
Coral: Neon Green Candycane, Brown Candy Cane, Purple and Blue Candycane, GSP-green, Palythoas, Montipora Digita (Green and Purple), Montipora Nodosa, Acro's, Neon Green Favia, Sun Coral, Cynaria, Zoanthids
Shrimp: Skunk Cleaner Shrimp, 2 Peppermint Shrimp, Tiger Pistol Shrimp
Clam: (2) Crocea,


That's what I love about saltwater tanks. You get God's best!!
deaclauderdale is offline   Reply With Quote
Old 02-09-2007, 03:38 PM   #19 (permalink)
burning2nd
Acropora
 
burning2nd's Avatar
 
Join Date: May 2006
Location: Pocono PA
Posts: 1,958
Re: electrical

i have a seprerte box for the hole bassment...

3x30amp i think... (10-15 outlets)

im runin my tank off 2 outlets..
__________________
________________________________________________
30g, 10g DIY sump w/ mag7
Csr90 over flow.
36" sunpod 2x150
2 Tunze 6020
40 Lb's Live Rock
20 lb's of Ls
Aqua C REmora


mIxed reef, softies, pora's, clams,
1 Amphiprion ocellaris (hosting GTA)
2 cromies and one dragon
jake the jedi sexy shrimp, and brown bob
burning2nd is offline   Reply With Quote
Old 02-09-2007, 03:58 PM   #20 (permalink)
billyr98
Reefing Addict
 
billyr98's Avatar
 
Join Date: Nov 2005
Location: Cherry Hill, NJ
Posts: 5,400

My ReefSpace
Add yours!
Re: electrical

Quote:
Originally Posted by deaclauderdale View Post
Billy do you have any pics of your electrical setup?
I will get some if you are interested....
__________________
Billyr98

-=NJRC Treasurer=-

My 450g Reef Tank ~~~ Its HERE!!!
billyr98 is offline   Reply With Quote
ReefSanctuary Sponsor
Old 02-09-2007, 04:00 PM   #21 (permalink)
billyr98
Reefing Addict
 
billyr98's Avatar
 
Join Date: Nov 2005
Location: Cherry Hill, NJ
Posts: 5,400

My ReefSpace
Add yours!
Re: electrical

Quote:
Originally Posted by burning2nd View Post
i have a seprerte box for the hole bassment...

3x30amp i think... (10-15 outlets)

im runin my tank off 2 outlets..
It might seem good to run 30 amp lines, but it is not! Outlets are rated for 15 or 20 amp for our pumps and lighting and such.. a 30 amp line would be for a dryer or something bigger, AC unit...
__________________
Billyr98

-=NJRC Treasurer=-

My 450g Reef Tank ~~~ Its HERE!!!
billyr98 is offline   Reply With Quote
Old 02-09-2007, 05:45 PM   #22 (permalink)
KodiakBear
Plate Coral
 
KodiakBear's Avatar
 
Join Date: Sep 2006
Location: Woodbine, GA
Posts: 790

My ReefSpace
Add yours!
Re: electrical

Quote:
Originally Posted by billyr98 View Post
It might seem good to run 30 amp lines, but it is not! Outlets are rated for 15 or 20 amp for our pumps and lighting and such.. a 30 amp line would be for a dryer or something bigger, AC unit...
Alright, I'm not licenced yet outside of the military, so I'm likely wrong... Yet, isn't the breaker rated such to protect the wire from overheating from excessive I2R losses at higher currents? A 30A breaker is rated for wire no smaller than 10 AWG for this reason, is it not?
If something faults as such to create a short, will not a 30A bkr still protect the system, or are you saying that the smaller equipment would not be able to trip a 30A Bkr even when faulted?
As for the GFCI outlets, I have one installed next to my tank so as to allow for that to trip the system while leaving the rest of my home's electrical intact. My tank is all connected to one 20A breaker via two GFCI protected outlets; granted, my system is small enough that I'm not going to have to worry about coming close to maxing that out. (running about 11A total)
__________________

Isaiah 6:8
I once prayed God would grant me patience. The next day I was starting a reef aquarium.
My Confession
KodiakBear is offline   Reply With Quote
Old 02-09-2007, 10:39 PM   #23 (permalink)
billyr98
Reefing Addict
 
billyr98's Avatar
 
Join Date: Nov 2005
Location: Cherry Hill, NJ
Posts: 5,400

My ReefSpace
Add yours!
Re: electrical

yes 30a breaker for 10awg wire.. But you shouldn't connect a 30amp breaker to a 20amp outlet device....
__________________
Billyr98

-=NJRC Treasurer=-

My 450g Reef Tank ~~~ Its HERE!!!
billyr98 is offline   Reply With Quote
Old 02-09-2007, 10:42 PM   #24 (permalink)
emo_1992
Bryozoan
 
emo_1992's Avatar
 
Join Date: Jan 2007
Location: Idaho Falls, ID
Posts: 47
Re: electrical

Billy would you suggest then running to seperate and aditional 20 amp lines to the tank then with GFCI outlets?
emo_1992 is offline   Reply With Quote
Old 02-09-2007, 10:43 PM   #25 (permalink)
billyr98
Reefing Addict
 
billyr98's Avatar
 
Join Date: Nov 2005
Location: Cherry Hill, NJ
Posts: 5,400

My ReefSpace
Add yours!
Re: electrical

i recommend GFCI near the tank... 2 seperate 20amp lines would do fine..
__________________
Billyr98

-=NJRC Treasurer=-

My 450g Reef Tank ~~~ Its HERE!!!
billyr98 is offline   Reply With Quote
ReefSanctuary Sponsor
Reply

  Reef Sanctuary > Main Forums > Equipment



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 04:19 AM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0 RC8
©2003-2007 Centropyge Productions LLC
vB Ad Management by =RedTyger=


Page generated in 0.17607 seconds with 11 queries

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151